I have worked in the industrial environment for 30 years but recently ran across a situation I have never seen. That situation is that a 480 volt, 3-phase, 400 amp panel is being fed from two (2) separate 200 amp, 480 volt disconnect switches. Seems to me this could present some serious issues. I was just looking for opinions on this. Thank you in advance for your input.
 
Welcome to the forum. Please update your profile as to what type engineer.
Yes this presents serious safety issues.
 
The one comment seemed sufficient.. it is a safety issue and is a violation of 240.8
 
I have worked in the industrial environment for 30 years but recently ran across a situation I have never seen. That situation is that a 480 volt, 3-phase, 400 amp panel is being fed from two (2) separate 200 amp, 480 volt disconnect switches. Seems to me this could present some serious issues. I was just looking for opinions on this. Thank you in advance for your input.
Can you post a pic of your situation? That generally stirs conversation.
 