10A breakers have been around for decades as supplemental protection. It is only recently that the NEC has allowed them for branch circuit protection.I note the 2023 NEC now lists 10 amps as one of the :Standard Ratings" in Table 240.6(A)
I've seen a few SqD QO10 in the past
They have been a Square D QO product for years. Certainly this is not supplemental, as they fit Load Centers. Unless you mean supplemental to the main breaker.It is only recently that the NEC has allowed them for branch circuit protection.
Its an ERV. I assume that could be done. By what everyone is saying though, I will call for the 10A breaker and see what happens.Does this need it's own/dedicated 10 amp circuit or can you grab a nearby 20 amp circuit and put a fuse in-line to this device? (What is this thing, anyway?)