MOCP 10A?

Status
Not open for further replies.

Rock86

Senior Member
Location
new york
Occupation
Electrical Engineer / Electrician
Anyone installing a 10A circuit breaker? I have a manufacturer's cutsheet calling for an MOCP of 10A. I have been seeing this more and more. 1675181036791.png
 
I note the 2023 NEC now lists 10 amps as one of the :Standard Ratings" in Table 240.6(A)
I've seen a few SqD QO10 in the past
 
I note the 2023 NEC now lists 10 amps as one of the :Standard Ratings" in Table 240.6(A)
I've seen a few SqD QO10 in the past
10A breakers have been around for decades as supplemental protection. It is only recently that the NEC has allowed them for branch circuit protection.
 
Even though 10 amp became a standard OCPD rating only in the 2023 code, manufacturers have had them available for a long time...I installed some 30+ years ago.
 
It is only recently that the NEC has allowed them for branch circuit protection.
They have been a Square D QO product for years. Certainly this is not supplemental, as they fit Load Centers. Unless you mean supplemental to the main breaker. :unsure:

I''ve not used one in a residential panel yet, but have in industrial panels.
 
Does this need it's own/dedicated 10 amp circuit or can you grab a nearby 20 amp circuit and put a fuse in-line to this device? (What is this thing, anyway?)
Its an ERV. I assume that could be done. By what everyone is saying though, I will call for the 10A breaker and see what happens.
 
Looking at the data sheet.
I would say no it would not require a deducted circuit.
We usually use a fused switch at the unit.
Install a 10 amp fuse.
The switch will serve as disconnecting means at unit.
Handy box or single gang box SSU, four square box SSY.
 

Attachments

  • Screenshot_20230131-165916.png
    Screenshot_20230131-165916.png
    211.8 KB · Views: 10
Years ago Kidde required a 10 amp breaker on the FACP we installed for Halon suppression systems
 