Say you had multiple receptacles located long a wall and combined it was 6(1P-20A) circuits and you had to run EMT through the studs from/to each receptacle.
Assuming separate neutrals what would be the most #12's you you put in a 3/4" pipe?
What I come up with is:
#12 @ 75 degree is rated for 25A.
4-6 CCC's in a conduit would need to be derated and only good for 80%. Thus 4-6 CCC's(neutral counted as CCC) would be good for 20A after derating.
So 6 #12 CCC's in a 3/4" conduit is the max, correct?