electrofelon
- Cherry Valley NY, Seattle, WA
- Electrician
I have a mass spectrometer that I need to provide a UPS for. The machine consists of 3 components, and take a 230/400V supply:
1. The main machine is 8A @ 230V (L-N)
2. RF generator is 10A @ 230V (L-N)
3. Vacuum pump which is 7A three phase (400V)
IF I put the main machine and RF generator on different phases, I get a max phase current of 17A. I am just going to assume a UPS cant put more than a third of its rating on one phase, so assuming 17A on ALL phases I get 12KVA. We were originally looking at a 20KVA/18KW UPS, however I am a bit concerned about start up current of the pump, PLUS someone we were speaking to from the UPS manufacturer said this:
I am a little skeptical of some of that. For one thing, the pump will not be repetitively cycling, probably just on and off a few times per day. Also I find the comments on unbalanced systems to be kinda misleading. More heat in the wiring? Rise in neutral current? Stress on transistors? Well if you are designed and spec'ing around a known imbalance and are well within all specs, I am not seeing that as an issue.
My thinking is if we go with a 30KVA/27KW unit, that should cover the startup current of the pump (its nameplate is actually 4.8, not the 7 shown on the general spec sheet). and should provide plenty of extra capacity for any inductive loading of the pump. So I just wanted to see if anyone had any comments or experience. I know there is no definite answer here as they just dont provide any specifics of allowable types and percentage of loading, other than their comment "its not really designed for inductive loads". Seems to me oversizing the unit which would also account for the inrush, would provide plenty of robustness and make the inductive load component a relatively small portion of the nameplate output. I have attached a picture of the vacuum pump.
We escalated this to our 3 phase expert and he provided this feedback:
I am afraid we do not have a solution for this application.
First, our UPSs are not really designed for inductive load applications. Any loads containing, pumps, motors, compressors and/or any components that produce high inrush in a repetitive cycling which is very harsh on the internal components of the UPSs. The customer may end up purchasing an expensive system that will experience premature wear resulting in system failure.
In terms of unbalanced loads, to be honest there is not a perfect customer out there that has a perfect balanced loads, however our engineering team calls for the recommended line-to-line load unbalance to be less than 50%. That would be another concern for this application. Remember that an unbalanced system produces more heat in the wirings , rise in neutral current, stress on the transistors etc.