Hi all, new to this forum but have been reading for a long time. Want to say thank you to all you guys as you have educated and helped me with many things.
I was recently doing a small job. I moved a light to center it from the room. This is an older home I'm assuming around 60s due to the anaconda romex in the house. The power is at the light and just one 14-2 without ground down to the switch. The light had quite a few other wires in it supplying receptacles and power over to other bedroom lights. I junctioned these all in the attic with a 2 gang. When I came down to test the switchleg and make sure I got the right wire from the switch hooked up to the light my hot stick was going off with the switch off. I removed the switch completely to open the switchleg and my hot stick was still going off. I then used my DMM to check voltage. I was getting 50 volts from hot to neutral at the light. When I tied the switchleg back to power I got proper 120 volts. With the switch off I hooked the light up to the hot and neutral. This made the voltage reading go from 50 volts between hot and neutral down to millivolts. Also when using my wiggly I got no voltage reading with the switch off and 120 volts with switch on.
This is my first time running into this. From what I have read I believe this is capacitive coupling from the switchleg wire. The swirchleg wire is in the box with all the power junctioned. One of the wires is tied in with all power and all power going down to the switch. The other wire Is tied into the new wire I ran out of the box to hit the new light box location.
This voltage concerned me a little bit. I first wanted to make sure things were bonded correctly. They appear to be bonded properly in the panel. #6 ground out to a rod, neutral is bonded to the GEC at the main panel. However I went from the metal fridge casing to A phase and read 55 volts with my high impedance DMM. With my wiggly I measured 0 volts. Could these be false readings due to my high impedance multi meter? Another note that may be important is this home has no equipment grounds on the majority of circuits due to the anaconda romex without an EGC.
I was recently doing a small job. I moved a light to center it from the room. This is an older home I'm assuming around 60s due to the anaconda romex in the house. The power is at the light and just one 14-2 without ground down to the switch. The light had quite a few other wires in it supplying receptacles and power over to other bedroom lights. I junctioned these all in the attic with a 2 gang. When I came down to test the switchleg and make sure I got the right wire from the switch hooked up to the light my hot stick was going off with the switch off. I removed the switch completely to open the switchleg and my hot stick was still going off. I then used my DMM to check voltage. I was getting 50 volts from hot to neutral at the light. When I tied the switchleg back to power I got proper 120 volts. With the switch off I hooked the light up to the hot and neutral. This made the voltage reading go from 50 volts between hot and neutral down to millivolts. Also when using my wiggly I got no voltage reading with the switch off and 120 volts with switch on.
This is my first time running into this. From what I have read I believe this is capacitive coupling from the switchleg wire. The swirchleg wire is in the box with all the power junctioned. One of the wires is tied in with all power and all power going down to the switch. The other wire Is tied into the new wire I ran out of the box to hit the new light box location.
This voltage concerned me a little bit. I first wanted to make sure things were bonded correctly. They appear to be bonded properly in the panel. #6 ground out to a rod, neutral is bonded to the GEC at the main panel. However I went from the metal fridge casing to A phase and read 55 volts with my high impedance DMM. With my wiggly I measured 0 volts. Could these be false readings due to my high impedance multi meter? Another note that may be important is this home has no equipment grounds on the majority of circuits due to the anaconda romex without an EGC.