wwhitney
- Berkeley, CA
- Retired
I've only looked at a couple minisplit outdoor unit nameplates, but the ones I have looked at list compressor RLA, fan FLA, and MCA. And it's not the case that MCA = 1.25 * RLA + FLA, MCA is larger than that.
Is this because the outdoor unit typically provides power for the indoor unit, so the MCA includes the load of the indoor unit? In which case for outdoor units that can connect to multiple indoor units, the MCA would have to include the worst case configuration in terms of number and size of indoor units. In that scenario, is there any path in the NEC for determining the actual load / MCA for the given installation, rather than using a worst case nameplate rating?
Thanks,
Wayne
Thanks,
Wayne