Jhallelec
- Connecticut
- Electrical
Has anyone ever been failed for installing a 4/0 SEU cable in a 2” pvc from meter to a LB as a stub into the house and converted over with a FA connector.
Just guessing…but I am thinking that one of the issues maybe that the 2” LB is not big enough for the 4/0 SEU. Also there may be an listing issue for converting from the FA to a SEU Cable connector.Has anyone ever been failed for installing a 4/0 SEU cable in a 2” pvc from meter to a LB as a stub into the house and converted over with a FA connector.
I doubt there are any instructions or listing documents prohibiting threading a camp connector into an FA, but one could argue that the Connector needs to bonded and is not.Just guessing…but I am thinking that one of the issues maybe that the 2” LB is not big enough for the 4/0 SEU. Also there may be an listing issue for converting from the FA to a SEU Cable connector.
Are you using the connector for 312 5 C ?Has anyone ever been failed for installing a 4/0 SEU cable in a 2” pvc from meter to a LB as a stub into the house and converted over with a FA connector.
The issue is usually that the 5X SE cable minimum radius of the bend in the LB cannot be maintained. An elbow in lieu of the LB solves that problem.
I have oversized the LB before to make it large enough for the 4/0 SEU!Has anyone ever been failed for installing a 4/0 SEU cable in a 2” pvc from meter to a LB as a stub into the house and converted over with a FA connector.
There are ways to do it without the Shepard's hook and still use the code compliant elbow.Which would be an interesting turn into the house from an outside meterbase without some big ugly sheep hearders hook to contend
You're correct that in some installations an elbow may not be a suitable replacement for an LB due to the length of the sweep.If a 4/0 SEU cable is traveling down an outside 3 1/2"deep wall, are you still not having to make as sharp a bend to turn it 90 degrees out?
His inspector seems to be very "Code oriented" and it's likely the individual conductors would not meet 314.28 with a standard PVC 2" LB.SEU has individual conductors that are labeled as one of the types permissible in any Chapter 3 wiring method, if I'm not mistaken? In which case what's wrong with using a cable clamp at the house end of the PVC stub and stripping the SEU jacket inside the PVC? The cable clamp becomes a conversion fitting from cable to PVC.
Cheers, Wayne
There's 314.28(A)(3), so what's the typical marking on the interior of a 2" LB? If it's 3 @ 4/0, then it's fine. If it's less, then I agree a 2" LB is sized too small for the application.His inspector seems to be very "Code oriented" and it's likely the individual conductors would not meet 314.28 with a standard PVC 2" LB.
Per the "tech drawing" available near the bottom of this page, for Cantex 2" LB, it's (3) 4/0 XHHW. So 314.28(A)(3) would be complied with.There's 314.28(A)(3), so what's the typical marking on the interior of a 2" LB?
The inspector said the bend radius is wrong. If you use a sill plate the bend radius is even smaller.Has anyone ever been failed for installing a 4/0 SEU cable in a 2” pvc from meter to a LB as a stub into the house and converted over with a FA connector.
I assumed that was his issue and I have to agree with him. Many inspectors will let it slide. My own home has #4/0 SEU in a 2" PVC LB that somehow passed inspection.The inspector said the bend radius is wrong. If you use a sill plate the bend radius is even smaller.