Hello everyone,
I am sizing an electrical panel (240/120v rated 125A) for a new industrial process building. The panel is only serving building-related loads, i.e. lighting, receptacles, exhaust fans, heater fans, and a few control panels. So far I only have around 22 amps of load calculated, and 11 of 24 circuits are occupied. With consideration of possible future loads, how would you guys size the feeder conductors and the transformer (480:240/120) feeding the panelboard?
If you size it off of the load I'd be looking at 10 AWG feeder conductors with a 7.5kVA transformer. However this feels short-sighted to me and the right thing to do feels like to size the feeders and transformer to max out the panelboard capacity of 125A, giving you feeder conductors of 1/0 w/ #6 ground and a transformer of 25 kVA.
Somewhere in the middle seems reasonable, like installing a 100 MCB in the panelboard, and feeding it with #2 (#8 Ground) but keep the 25 kVA transformer in case the MCB needs to be upsized.
This is a perennial quandary for me as I am more of a controls guy, an opinion from someone who typically installs/sizes equipment like this would be of great help.
Thanks
Thanks