tuckerch
New User
- South Carolina
- Maintenance
Hello everybody,
Recently at work, we lost a circuit that blew underground. The court has 6 gooseneck LED lights fed by two individual 208V circuits, with one circuit being down half of the lights stopped working. We called electrical contractors out and to resolve this issues, they capped the bad wires, upped the good circuit breaker to a 50A (originally 2 20A breakers fed it) and set a sub-panel being fed off the bottom of the contactor. In said sub panel, there are two 20A two pole breakers feeding the tennis court lights. Said lights work properly now, but here is my dilema.
My boss claims the sub panel needs a neutral wire (sub panel is 150 ft from main breaker), sub panel is for 208V equipment only. He claims also, because of distance, that the sub panel needs a ground rod drove and the sub panel needs to be bonded to the ground rod. He also claims because the distance is 150 to feeding breaker that they couldn't up the breaker size.
I consulted my old boss about these topics and I was given the answers that I told my current boss (there is no problem) but my current boss continues arguing with me stating he is right and I was taught by hillbilly electricians. So what do you think? Can you pull NEC codes from the book about sub panels needing a neutral for 208V only equipment, upping breaker sizes on long runs and driving a ground rod for long runs? I was told to post this here!
Oh btw, my boss has been a handy man for 15+ years, I did electrical work for 15 mo and my old boss has nearly 20 years of experience doing electrical work.