I don’t see we’re that states that there a gfci for higher harmonics
Try a Siemens brand GFCI. This has fixed multiple tripping for me on pool pumps with inverters. Commercial raypak MVB and Xtherm boilers and some ACs having issues. They have somehow figured out how to filter out noise from actual ground fault leakage. And yes sometimes this means I install a small spa pack disconnect with a siemens gfci breaker.But, hang in there ... Until September 1, 2026 !
I also don't think listed HVAC equipment need GFCI when hardwired properly. Expanding GFCI to all exterior outlets was an over reach without proper cause.
Most of my pool work is all Commercial pools that are required to have pumps running while in use by health department. So not on option on those.. Siemens also worked great on m multiple AC units.Until this is all worked out, I turn the power off to the pool when in use. Just to be safe !
It's my belief that "Harmonics" are the culprit in this situation.
Please "Stand By" ... There should be an answer by September 1, 2026 !It's been well known for many years the harmonics from equipment that uses VFDs causes problems with GFCIs. This is nothing new.
There was a big problem with Pentair when they started using VFD pool pumps that had to be supplied with a GFCI. One manufacturer (Siemens?) even designed a special breaker for the application. Of course, it had to be installed in a Siemens panel. I don't know ultimately what the fix is, not sure if Pentair redesigned their pump motor drive to eliminate tripping normal GFCI breakers.
So, now that the NEC wants outdoor A/C units supplied with a GFCI protected circuit, we're back to the same problem. It's going to have to be up to the A/C equipment manufacturers to redesign their equipment to eliminate tripping whatever the cause.
-Hal
For your own pool do what ever you want.For safety reasons, no one in the pool when the power is on.