3/4" is the correct size. No need for any calculations where the conductors are of the same size. You can use the tables in Annex C. The table for RMC is Table 9.344.20 Size.
(A) Minimum.
RMC smaller than metric designator 16 (trade size 1⁄2) shall not be used.
It looks like that is table c-9.
Try C-8 for RMC.
Here is a tip.
All al blank continued headers insert table reference (RMC).
For PVC use ( sch40) or ( sch 80) and so on so you don't use incorrect table.
I trick up the the help with this at times then they learn to mark.
| C.8 — Liquidtight Flexible Metal Conduit (LFMC) | 803 |
| C.8(A)* — Liquidtight Flexible Metal Conduit (LFMC) | 806 |
| C.9 — Rigid Metal Conduit (RMC) | 807 |
| C.9(A)* — Rigid Metal Conduit (RMC) | 810 |
| C.10 — Rigid PVC Conduit, Schedule 80 | 811 |
| C.10(A)* — Rigid PVC Conduit, Schedule 80 | 814 |
| C.11 — Rigid PVC Conduit, Schedule 40 and HDPE Conduit | 815 |
| C.11(A)* — Rigid PVC Conduit, Schedule 40 and HDPE Conduit |
An unfair problem they could give, would be to give you a 2-conductor situation, with a 24" or less length, expecting you to take credit for the nipple rule.I would have said 3/4" also but, since they did not give you a length and asked for minimum you could say 24" or less in which case it woudl be `1/2"
This is NEC 2020, has that one changed ?The table said View attachment 2564136
I got you, thanks.The use of trade size 3/8 while provided for in the listing standards is not permitted to be used in an NEC application. In addition, only five of those conductors fit in a 1/2", so no way eight fit in 3/8".