600 kcmil Al= 340 amps*2= 680 amps, no good next size up is 700 amps. Those conductors are too small for 800 amps.We’ll 600 aluminum do the job with my 2 conduits
Is that a high-leg delta? (Neutral and high leg could be smaller)I’m working on 3ph 800A 120/240 service
I ran 2 4” conduits underground total wire run we’ll be 120’. What size aluminum wire can I use
no High leg. Running 4” PVCIs that a high-leg delta? (Neutral and high leg could be smaller)
Metal or PVC conduit? (Metal could be EGC)
Service or feeder? (Will there be an EGC?)
My calc shows that eight 400s will fit in a 4" PVC conduit.
ServiceI think my best bet is to run 500MCM copper
serviceI think my best bet is to run 500MCM copper
Yes I have everything ready and mounted. Had to shop all over on line to collect it all.Hope you already have the gear, I’m looking at almost 10 months lead time for an 800 amp fusible 600 volt disconnect, and an 800 amp 277/480 three phase MB panelboard. Found two new 800 amp disconnects at a salvage place in Wisconsin, so instead of a 800 amp panelboard, I’m doing a wireway with off the shelf disconnects. Got to have the engineer re-draw it for the inspector.
That will work. 380*2=760 next size up rule 800 amps. You could also use two sets of 750 aluminum. 385*2=770 amps.I think my best bet is to run 500MCM copper
I get 4 sets of 300 kcmil Al in two raceways for the full 800 amps. 260*2*80%*2=832 amps. Raceway fill isn't an issue.
Just curious, why do you think 500 copper is better? I would much prefer the smaller aluminum personally. Can your equipment handle for sets per phase?I think my best bet is to run 500MCM copper
Why isn't this engineer specifying the conductors?Calculated load is only 550A but engineer is asking for 800A main breaker
Good question. And if he wants the full 800 amps then the installer will have to provide it. Since he already install the equipment he might be limited as to the wire size and how many sets he can actually use.Why isn't this engineer specifying the conductors?
If he specked 500 CU that is what he wants. If he does allow you to go with AL he'll probably be wanting a credit for the customer.He is asking for two sets of 500
Wanted to see if going aluminum we’ll be better price