- New Jersey
- Journeyman Electrician (retired)
A VFD with an input current of 28 amps is fed with #10 THHN is a raceway. Is this code compliant based on 240.4(G)?
I assume you mean with an OCPD larger than 30A, as with a 30A OCPD there would be no issue.A VFD with an input current of 28 amps is fed with #10 THHN is a raceway. Is this code compliant based on 240.4(G)?
Yes you're correct sorry I left that part out. The conductors and the OCPD are 35 amps (28*125%=35)I assume you mean with an OCPD larger than 30A, as with a 30A OCPD there would be no issue.
Yes that's the discussion we're having on the job."G" does not include 430 Part X in it's listing so an argument could be made the Part G exceptions do not apply