Did the unit come with a factory cord/plug? If so, that’s the receptacle you can plug in to. The manufacturer’s instructions should specify if a dedicated circuit is required. It’s probably a good idea for that size load.
The UPS probably doesn't work that way. Check its documentation. My guess is that it can output 1700VA but never draws more than 8A from the receptacle for charging, no matter what you're using. But check the documentation.I have to check the 15A or 20A cord end.
My concern that I'm thinking of though is that since the load is 1,700VA and if the batteries are charging (could be 2A up to 8A I've seen on some data sheets) then wouldn't the 1,700VA + 960VA (8A charging) overload the circuit? I know it would only be temporary to bring the batteries up to full charge. But still a concern?
But it isn't. That's the battery/inverter capacity. The load is whatever the UPS is powering.. . . since the load is 1,700VA . . .
That's true for ANY receptacle.With all that being said, you could still overload the circuit because it doesn't take into consideration what all else may be plugged into that circuit.
JAP>
Thanks.
Does 210.21(B)(2) or 210.23(A)(1) 80% max load for cord and plug come into play at all? Even though the UPS is supplying multiple outlets and no individual piece of equipment connected to the UPS would exceed the 80% rating of the circuit, could an argument be made that a UPS is a a "singular" cord and plug load (since you are plugging in a singular UPS plug into a duplex receptacle) and I would have to comply with this?