Garbage disposal gfci
domnic
Electrical Contractor
Do i need a gfci for garbage disposal 2011 nec ? ///////////////////////////////////////////////////////////////////////////
210.8(a) (6). 2011 nec . receptacles installed for disposals, dishwashers, trash compactors, are not required to be protected by GFCI.
They are if they are installed somewhere other than a kitchen and they would have to have a really long pipe connecting them to the sink not to be. 😁
I find it odd that the 2023 requires microwaves to be gfci protected but not garbage disposals connected to a sink
Well, in dwelling units it covers all receptacles in a kitchen (not just the countertop, a change from 2020) and any receptacle within 6' of a sink, with the distance measured through cabinet doors.
So that would cover almost every garbage disposal. I guess you could install a garbage disposal on a sink in a non-kitchen bar area with a cord longer than 6' that plugs into a receptacle sufficiently far from the sink, and then you could skip GFCI protection.
Cheers, Wayne