MJRobinson
Member
- Location
- Chico, CA, USA
The PV System main disconnecting means shall have ratings sufficient for the maximum available short circuit current that is available at the point if the PV system interconnectionn to utility.
Please provide fault current data for the existing electrical system, then match all new PV equipment rating witht eh existing AIC rating. 690.13(E); [2022 code 690.15(C)]
We got this from AHJ. Our breaker (QJ23B200) has 10KAIC, the MSP (1000A has a KAIC of 50KAIC)
Are they saying that we need a 50AKAIC-rated fused switch and can only tap?
Doesn't make sense.