I am working on a delivery room that has the following loads:
- On anesthesia boom: receptacles on critical branch circuit, receptacles on normal branch circuit
- On walls: general purpose receptacles on a normal branch circuit
- 4 dedicated critical circuits for 4 equipment in the room
- Surgical light on critical branch, dedicated circuit
- 2x4 ceiling lights on the critical branch circuit
- The normal receptacles also require and isolation panel, right? Because of their location in a "wet procedure location".
- I couldn't find a specific requirement in NEC 517.33 & 517.34 that prevents general purpose receptacles in a critical area from being on the normal branch, as those articles only include specific receptacles. Can you confirm?
- Is it acceptable to have two isolation panels, one fed from a normal branch 208/120V panelboard and one fed from a critical branch 208/120V panelboard? Maybe 5kVA each?
- The 2x4 lights are not required to be on isolated panels, and this circuit is shared with other lights in a nearby room. I don't think this would be a code violation, will it?