Two more 220 PIs today. I'm a little baffled on this one as to why or how the current wording could be there. So if I'm missing the point somehow and this PI isn't reasonable, please explain.
Cheers, Wayne
[I'm omitting a bunch of the text that doesn't change.]
220.83 Existing Dwelling Unit.
This section shall be permitted to be used to determine if the existing service or feeder is of sufficient capacity to serve additional loads. Where the dwelling unit is served by a 120/240-volt or 208Y/120-volt, 3-wire service or feeder, calculating the total load in accordance with 220.83(A) or (B) shall be permitted.
(A) WhereAdditional Air-Conditioning Equipment or Electric Space-Heating Equipment Is Not to Be Installed Present.
(B) WhereAdditional Air-Conditioning Equipment or Electric Space-Heating Equipment Is to Be Installed Present.
Statement of Problem and Substantiation for Public Input
The sole difference in the computations in 220.83(A) and 220.83(B) is that 220.83(B) specifies a 100% factor for any Air-Conditioning Equipment or Electric Space-Heating Equipment. Under 220.83(A), any such equipment would end up with a 40% factor. The current dividing line between 220.83(A) and 220.83(B) is based only on what new equipment is being installed.
So consider a two stage series of improvements to a dwelling unit, two separate projects under two separate permits, perhaps a year apart. The final stage may have a load calculation that differs depending on what order the improvements are done, even as the final installed result is the same. If all of the Air-Conditioning Equipment or Electric Space-Heating Equipment is added as part of the first stage, and the second stage contains no such equipment, the final load calculation will be subject to 220.83(A) and include only a 40% factor for the Air-Conditioning Equipment or Electric Space-Heating Equipment. Conversely, if the second stage improvement does include additional Air-Conditioning Equipment or Electric Space-Heating Equipment, then the final load calculation will be subject to 220.83(B) and include a 100% factor for the Air-Conditioning Equipment or Electric Space-Heating Equipment.
This difference in load calculation results for identical final configurations of equipment makes zero sense. Therefore I propose that the dividing line between 220.83(A) and 220.83(B) should be based on what equipment is present, not what equipment is being installed.
Please note that if this proposal is accepted, 220.83 may be further simplified by eliminating the A/B divide and just specifying the computation in 220.83(B) for all cases. I kept my proposal minimal for clarity.
Cheers, Wayne
(A) Where
(B) Where