Hey guys,
I came across a scenario that I was hoping to get some input on. Currently there's an existing delta-delta (center tapped) 75kVA transformer that feeds a single phase panel. Because this panel has 120V loads, I'm assuming it's wired across the A-N-C phases (assuming B phase is high-leg) since that's the norm.
We're looking to install another 120/240V single phase panel, but with the existing loads and proposed new loads, the 25kVA windings across A-C will not have enough capacity to handle all that load.
I'm thinking about adding the single phase panel across B-A (or B-C), but also bring the neutral along to this panel. I would install a label saying no 120V loads on the B phase, since that's still the high leg, but across A-N we should still get 120V. I've never really seen it done this way, so I just wanted to be sure this was possible. The more I think about it, the more I can't find a reason why not, so thought I would ask here.
Has anyone come across this? Any help/input would be appreciated!
Thanks guys!
Thanks guys!