SunNinja
- Washington
- Electrician
2020 NEC
I have a new situation. I believe I will need to do a Load Side Tap, and I want to see if I'm interpreting the rules around it correctly.
Existing:
Meter main combo, with 2 x 100A breakers. One supplies a hot tub. The other supplies a manual transfer switch for their backup generator, which then supplies MSP.
No room between meter and 100A breaker to do a line side tap - the rules surrounding that I'm comfortable with.
Solar is only 20A, we are protecting and sizing wire at 30A (microinverters can handle up to a 30A string, future expansion possiblility).
I need to interrupt either 100A feeder and tap off for the solar connection.
I'm reading 705.12(B)(1&2) to say that the portion of the run between your solar connection and the Load needs to be (125%solar) + (OCPD for Feeder). Opinions?
Makes sense, as the house could potentially pull 100A off the grid and SolarAmps at the same time.
Also, I am trying to figure out why I believe ANY tap will need a fusible 60A rated disconnect, even if fused down to 30A. It would seem that it is only required on supply-side tap because the disconnect can be perceived as subject to service disconnect rules. So - can a load side tap just be a 30A fused disconnect?
Existing: