TwoBlocked
- Bradford County, PA
- Industrial Electrician
First some background. A site had 480V 3-phase service. One of the feeders went to a transfer switch to provide back-up power from a 480V 3-phase generator. The loads were from some 3-phase air compressors, a large 480V-120/240 split phase transformer feeding an MCC, and a very small 480V-120/240 split phase transformer feeding a panelboard with hardly any load.
One fine day during a planned outage the genny and transfer switch did their job, then the genny tripped out a minute later. Upon investigation it was noted that it tripped on current imbalance, which was set at 25%. (Somehow this had gotten changed from the original 75%). The only 3-phase demand was the 3 air compressors which were programmed to wait a few minutes after a power restoration and then come on one at a time as needed. No surprise it tripped with the low imbalance trip and nearly no load on one of the legs.
My suggestion was to install a 277V-120/240 split phase transformer and feed both the small panel board mentioned and a larger one fed from the MCC. This would remove some of the load from the 2 legs feeding the large transformer and move it to the remaining single leg going to the additional transformer. I doubt they did so and probably just left things like they were. (Been job hopping lately...)
But I got to thinking about this and have a question. Let's say the change was accomplished and the large transformer drew 50 amps on phases A to B while the small transformer drew 50 amps on phase C to neutral. I am used to thinking that if all the legs draw the same amps, there is no neutral current at the source. Or is that only the case with split phase?