Shaneyj
- Katy, Texas
- Project Engineer
I've got a facility with a 240V open delta service.
This is my first personal experience with an open delta service.
I don't know his service size but utility transformers are 50 and 100kVA.
My reading has led me to understand that because only 2 transformers are supplying all 3 phases - of the 150kVA - only 130k is available (86%). Is this correct?
The customer needs to power some 3 phase 460V equipment, so I'll be sourcing a transformer: 240V delta primary to 480Y secondary.
He's got 2 machines with a possible maximum load of 51.2kW. One of those loads is a 40HP motor operating a vacuum pump - the other is a CNC, so a couple small motors and some electronics.
After the 86% from the open delta is applied (assuming that is correct) do I treat the rest of the calculations using typical 3-phase math? Do I need to figure for some other loss or "open delta factor" at the step up from 240V to 480V?
Proposed Topology: Existing 240V paneld board --> Fused disconnect for XF Primary --> 240D-480Y/277 step up XF --> 480V panel --> branch circuits to respective loads
Anything else to look out for?
. The theoretical answer is you always let the power company know of an addition of load and let them do what they want!