wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
I would say the phrase "the higher ampacity shall be permitted to be used" has the effect of changing the ampacity. Since "used" is unlimited, we can use the higher ampacity for all purposes.I see nothing that actually changes the ampacity when you use the exception.
Whenever the bolded portion is true, there is no tap (assuming the whole thing isn't a tap). So if 310.14(A)(2) Exception covers the case of a lower ampacity due to a reduction in conductor size, then there is no tap.Just like a lot of other rules, the exception simply permits the conductor to be protected with an OCPD rated higher than the actual conductor ampacity.
The small conductor is a tap and must be installed per the tap rules.
Anyway, because of this sloppy wording, I submitted a PI to change the start of the exception to "Where different ampacities apply to portions of a circuit of identical conductor size,"
Cheers, Wayne