310.15C1 of NEC says that in a raceway with more than 3 current carrying conductors you are to reduce the current carrying conductors ampacity according to NEC table per number of conductors
I did not find a place under this section 310.15C1 that would point to this only applying to the number of conductors over 30. The code simply says over 3 conductors. So how would someone know there would be some random code scattered among 900 pages of NEC code to contradict this?
Apparently 376.22 A & B does this. All this time I thought conductors in a raceway such as EMT conduit would have to be de-rated in ampacity if over 3 current carrying conductors
This has brought more confusing and I’m not sure which way to go?