That wire you see is from the melting that happened. They weren't stripped that far back.
Sent from my SM-G998U using Tapatalk
The three causes for this I have seen/heard of are:
Undertorquing the connection
Overtorquing the connection
Using copper only lugs to connect aluminum conductors
ggunn
Austin, TX, USA
Cu only lugs are rare nowadays.
But they are out there. I know of a case that happened a couple of years ago where nine SolarEdge Synergy Units were burnt up because the installer used copper only lugs to connect aluminum AC conductors to them.
pv_n00b
CA, USA
Professional Electrical Engineer
I don't think I have seen a terminal fail unless it was installed incorrectly or in an environment it was not designed for. These are really good terminals if used correctly.
jaggedben
Northern California
I go with one of the following:
- installed upside down and collected water
- lesser brand got too hot. I've seen Greaves melt through under normal conditions and I won't buy that brand again. Insulated housing melted through.
Figuring either of these happened in close enough proximity to ground or another conductor.
electro7
Northern CA, US
Electrician, Solar and Electrical Contractor
Can anybody help me understand what these Wagos are rated for?
I'm assuming in the US we go by the UL listing. Are the other listings for other countries?
But what would PV wiring be, the "building" wire that it lists?
rambojoe
phoenix az
Wireman
The rating is listed in your hand... what do you not decipher?
electro7
Northern CA, US
I wanted to confirm that solar branch circuits are considered "building wire"? (I assume they are)
Are they rated for DC voltage?
I've seen these burnt up in a DC system before, but I'm not sure what the cause was from.
In my above post- are the other designations to the left listing agencies in other countries and not something we go by in the US?