The electron man
- Nyc
- Electrician
nicked them ? Please explain thanks againThey are stripped long enough but they were stripped incorrectly, you nicked them.
Is there any chance of a line to line arc in a 480v with some exposed wire as shown ?Green tag from me.
Ron
No. Personally I like the insulation to be right up against the terminal but that is not a code requirement. We use a sharpie to mark the exact length and after a dry fit if it's too long we trim the bare conductor to the proper length.Is there any chance of a line to line arc in a 480v with some exposed wire as shown ?
I don't see it as being any worse than the bare lugs.Is there any chance of a line to line arc in a 480v with some exposed wire as shown ?
I do intentionally leave a bit sticking out so that the DE-OX is visible. Not that much but 1/8 inch is good.No. Personally I like the insulation to be right up against the terminal but that is not a code requirement. We use a sharpie to mark the exact length and after a dry fit if it's too long we trim the bare conductor to the proper length.
My journeyman likes it done this way , he claims it allows the strands to spread and make a better connectionNo. Personally I like the insulation to be right up against the terminal but that is not a code requirement. We use a sharpie to mark the exact length and after a dry fit if it's too long we trim the bare conductor to the proper length.
No offense to your J-man but that sounds like a bit of nonsense. I've never heard that one in nearly 40 years in this business and to me it's far from aesthetically pleasing which is part of the installation.My journeyman likes it done this way , he claims it allows the strands to spread and make a better connection
I've never seen overheated conductors because of this eitherNo offense to your J-man but that sounds like a bit of nonsense. I've never heard that one in nearly 40 years in this business and to me it's far from aesthetically pleasing which is part of the installation.
No. The lugs are closer together than the stripped wires. But yes as bit shorter on insulation. You would find it’s faster to tighten lugs with Allen socket on ratchet wrench, or likely you have a torque ratchet wrenchIs there any chance of a line to line arc in a 480v with some exposed wire as shown ?
Our working standards allows an 1/8.I do intentionally leave a bit sticking out so that the DE-OX is visible. Not that much but 1/8 inch is good.