Dark Sparky
- USA
- Electrical Engineer
Sort of the longer story but I have an apparently failed hot tub disconnect. That was discovered a while back, but now I have another issue in attempting to replace it. The original issue was that upon one of our power outages, the GFI function of the hot tub disconnect ceased working. That rendered the hot tub without power. For about 6 months now it has been wired straight through ( we have not been using the tub) but this allowed it to keep cycling and filtering.
Now I am going to replace the disconnect with a similar one. Upon opening it, I found that one of the wire nuts is melted. Picture attached. This is a 50 amp, 2 pole, breaker. So that should be 240 volt single phase. There are three wires coming from the panel, red, black and white. The same colors run out from the box to the hot tub. The only other aspect is that the red and white wires coming from the hot tub are very short, so there are approximately 12 inch jumpers. It is the connection between the short red wire coming directly in from the hot tub, and the jumper cable, which has the melted wire nut.
I'm hoping this is simply a poor connection, but looking at the thread linked below, it seems like there are some potential other issues?
Insight welcome - I want to keep my family safe!
Potentially similar issue? -
Melting wire nuts
Here is the situation. I can't find the cause. In wiring a bathroom addition the building contractor uncovered many wires in a floor that had been covered up. Some of these were hot some were not. We were able to pull the wires into accessible j-boxes. After all the wiring, the contractor...
forums.mikeholt.com