Right I get it now. Thank you.CR3 is open. That's the only way there can be voltage across it. Closed contacts have no voltage across them.
Could you answer the rest?
The fact that there is 120v between B and C indicates that CR must be open, and that the rest of the contacts must be closed.How can there be voltage between B and C if there's no voltage between A and B?
Leak through to where?120 volts with no load voltage will lek through the light bulb
That was supposed to be CR3.The fact that there is 120v between B and C indicates that CR must be open, and that the rest of the contacts must be closed.
Not even very large. Somewhere in the plus side of 100mv. That and side by side comparisons.Funny how many guys don't think to measure voltage across a set of contacts. That will tell you if the contacts are open, closed or there is a problem with them. For instance, a large voltage from the line to load side of contactor contacts will tell you that there is high resistance and likely the contacts are burned or on the way out.
-Hal
Same with checking for blown fuses on a circuit that has a load.Funny how many guys don't think to measure voltage across a set of contacts. That will tell you if the contacts are open, closed or there is a problem with them. For instance, a large voltage from the line to load side of contactor contacts will tell you that there is high resistance and likely the contacts are burned or on the way out.
-Hal
Yes, or across breakers. These checks are your basic fall-of-potential tests.Same with checking for blown fuses on a circuit that has a load.
CR2 thru CR5 are relays. The drawing shows contacts operated by said relays (they happen to all be NO contacts) Most of us would take "energizing the relay" to mean apply voltage, within rating, to the relay coil if there is no other specific information to mean otherwise. Those contacts are going to change state when that happens.CR2 thru CR5 are shown as contacts on the drawing yet the questions describe them as "energized" not closed or open I don't love it but we know what they meant to ask I guess....
You not the only one..........How are you seeing all that detail in the OP's image? For me it is too blurry to read any of the text or the labels on the drawing.
My vision isn't great, but I could read the labels without glasses and without increasing display magnification.How are you seeing all that detail in the OP's image? For me it is too blurry to read any of the text or the labels on the drawing.