lafredo
- Middletown, CT
- Electrical Engineer
Hello All,
I'm excited to share something I've been working on for the last several weeks. Below are (3) links to separate spreadsheets that have my NEC feeder sizing calculations. They linear in operation going top to bottom on the "Feeder Sizing" sheet (the others are tables and reference), the blue cells are inputs, and the grey cells are outputs/calculations. It starts by calculating the conductor ampacity with all deratings, then moves onto EGC selector, then Voltage Drop, and then upsizes the EGC if requested, and finally sizes the conduit and confirms wire selection. Please try it out, let me know if something is not right. Go forth and design, enjoy!
NEC Raceway, Cable, or Buried in Earth Feeder Sizing Spreadsheet
NEC Free Air or Cable Bus Feeder Sizing Spreadsheet
NEC Messenger Feeder Sizing Spreadsheet
Thanks,
Matt
Thanks,
Matt