NEC 314.16 B1 box fill
Jpflex
Electrician big leagues
Victorville
Electrician commercial and residential
To make sure I’m doing this right my metal single gang box measures 4”tall x 2/1/8” wide x 1/3/4” deep but NEC book only has similar box at 1/7/8” deep so I chose this?
Book gives total available volume of 13.0” for above box
Therefore the reason 4 x 12 AWG conductors
4 x 2.25 allowance At 9.0” take up
Plus 4 of 12 AWG ground conductors at 1 x 2.25 allowance at 2.25 take up
Plus 1 yoke receptacle under 2”wide is allowance at 2 x 2.25 take up
Added = 15.25 required allowance for a box labeled 13.0 total allowance is reason I can’t get receptacle and wires to fit
However the book does not mention allowance for internal pigtails such as if I were connecting 2 yokes together through the second receptacle pigtailed to the first receptacle in a two gang box
All the book says is give allowance for wires entering, entering and exiting without splice, if looped beyond minimum 6”? Conductor length from entering box point
What do you measure for pigtails for double gang metal boxes?
Double gang to be internal pigtail jumped from first receptacle to second receptacle where it is power fed
NEC does not specify allowance for jumpers
Also in NEC chart what is meant from device vs box for description as I don’t see single gang other than masonry gang?
314.16(B)(1) .... A conductor, no part of which leaves the box, shall not be counted.
A device box is commonly called a gem box, they come in single gang and can be ganged together to form a multi-gang box. For the square boxes (post #2) the cu in measurement is for the box with a blank cover and without an external mud ring or extension box.
A jumper or “pigtail?” Between receptacles, does NOT leave the box nor does it enter or exit the box but is simply made inside the box so I have yet to see what NEC says about the allowance for this as many jumpers can be made within
Jumpers don't leave the box so they don't count.
You don't count all the grounds (EGC), just one. Well I understand they changed that some, I don't have that code. Even with the change, you don't count all the EGCs.
I only counted grounds once for 4 grounds based on largest conductor and table