I am in OKC, Oklahoma, and I am having an issue here with my AHJ regarding MCA and MOCPD in regards to AC units.

Mike has several videos throughout the years pertaining to this issue and I have learned a lot from them.

When there is a nameplate, the job is pretty easy...IMO

In This situation, I have a 8-2 NMB installed on a 50A breaker at the panel.
Nameplate rating MCA 22.3 MOCPD 50A. I got this information late and played what i thought was a safe call.

I have referred my AHJ to article 240.4(G), which refers to 440, parts lll and Vl.

They have no desire to hear our point of view. They simply refer to 334.80, my understanding is that 440 relieves us from the ampacity constraint here on the conductors.

Has anyone won this debate in writing, anyone have a clearer code path than I?

I am being told that it explicitly that I have no chance here by the chief electrical inspector. I have made they changes they asked for due to not wanting to hold up the project. This isn't me trying to cheap out, its me trying to now prove the chief wrong. Thanks in advance
 
I'm afraid you are incorrect on this. Nothing changes the fact that NM has to use the 60 deg column. 240.4(G) or 440, doesn't give an exemption to use NM at 75 deg.
 
but..... he is using the NM at (actually below) it's ampacity) MCA 22.8
I fail to see the violation...
 
In This situation, I have a 8-2 NMB installed on a 50A breaker at the panel.
Nameplate rating MCA 22.3 MOCPD 50A. I got this information late and played what i thought was a safe call.
You could have #10 NM cable with the 50 amp OCPD for this application. Even #12 MC cable would be code compliant with a 50 amp OCPD.
 
Isn't a disco required at the unit? If it's fused, is the home run a feeder?

I know we've discussed it a lot, but I don't recall reaching a consensus.
Yes a disconnect is required at the unit unless the branch circuit device is within sight. I don't think there ever was a consensus to the feeder v. branch circuit argument but as of yet I see no mention of a fused disconnect in this thread.
 
Isn't a disco required at the unit? If it's fused, is the home run a feeder?

I know we've discussed it a lot, but I don't recall reaching a consensus.
It doesn't matter...440 sends you to 430 for feeders, and when you do the feeder calcs for a single motor it comes out identical to a branch circuit for that same motor.
 
It should be a fairy basic concept for an inspector or AHJ. There are a number of on-line articles that explain it and there is this Forum, of course, if you can get them to do a but of research but seemingly you have an uphill battle.
 
OKC should have a electrical board.
Get on the agenda lay it out for them and ask for a decision.
This will help educate them.

Give the construction industry board a call. They will help.
 

Attachments

  • Screenshot_20230525-181715.png
    Screenshot_20230525-181715.png
    85.8 KB · Views: 5
Also note that the MOCP is the MAXIMUM OC, you can go smaller, just not larger. At a 22.3 MCA, a 40A CB would probably be fine. Pass the inspection, then if the 40 nuisance trips, put the 50 back in.
 
Ask him to read 440.35 which sends him to 440.4(B)

If that don't do it go to the board.
Do every one there a favor.
Also note that the MOCP is the MAXIMUM OC, you can go smaller, just not larger. At a 22.3 MCA, a 40A CB would probably be fine. Pass the inspection, then if the 40 nuisance trips, put the 50 back in.
If the 40 trips ( doubtful) give the owner the inspectors number.
Agree 40 most likely be fine.

Have to wonder what size of conductor is in the whip. #10🤔
 
It doesn't matter...440 sends you to 430 for feeders, and when you do the feeder calcs for a single motor it comes out identical to a branch circuit for that same motor.
So what you're saying is that the feeder OCPD can be larger than the ampere rating of the conductors?
 