Jpflex
Electrician big leagues
- Victorville
- Electrician commercial and residential
Me and another guy at work will be attempting to properly cabinet ground (not system ground and not derive a neutral by owner’s choice) a delta concrete pad/slab 3 phase 4800/480 volt? transformer
There is the typical rebar 20 feet connected within the concrete lab connected to a typical copper rod with a stub up bend to be connected to transformer metal BUT NOT AT SYSTEM SECONDARY NEUTRAL POINT XO since this will be an ungrounded SYSTEM
There is a ground bolt connected to a wide thin ground copper looking strap with a hole inside it which looks to connect to a ground rod or grounding conductor somehow or some type of connector needed?
I have not checked if this connects to system XO / neutral point yet but if it does I cannot connect here but need to go to cabinet and bond somehow
Lastly the transformer will be powering all 3 phase motors and control circuits for motor starters but no line to neutral loads without another step down transformer downstream - another situation which may impede ungrounded system permissibility
From what I know the system must be installed with ground detectors in transformer secondary since this will be considered an ungrounded system
Ultimately how do we connect this ground rod to this pad mounted transformer? Thanks