Breaker rule
The electron man
Nyc
Hey my fellow electricians ,question about the 80% breaker rule
Where dose this rule apply I'm seeing different answers and I'm a bit confused
The 80% applies to the circuit when there is a continuous load. For example if you had a 20 amp non-continous load you could run that on a 20 amp circuit. If the load were continuous like lighting in an office building then you can only load the circuit to 80% or 16 amps.
When supplying a continuous load the breaker can’t be loaded beyond 80%. If you have a 100 amp breaker with a continuous load you can’t load it beyond 80% * 100 amps= 80 amps. If I you had an 80 amp continuous load you would need to size your overcurrent device at 80 * 1.25 = 100 amps. 1/.8 is where the 1.25 comes from. Unless the overcurrent device is rated for a continuous load. Your everyday breakers are not. You can look at 210.19(A)(1)(A) for branch circuits. A “Continous“ load is defined in article 100 as where the maximum current is expected to last for 3 hours or more. Good example would be a lighting load in a school that is going to be on all day long!
Do not forget your conductors are also sized based on continuous or non-continuous loads. It should not be a surprise that breakers are built and Listed to provide conductor protection.
Would this rule apply for a main breaker
So on a continuous load the ocpd and the conductors need to be rated at 1.25 ?
Dose this only apply to the branch circuits or a main breaker too , like a main breaker supplying the house or a building
Feeder or branch circuits.
215.3 Feeder Overcurrent Protection.
Feeders shall be protected against overcurrent in accordance with Part I of Article 240. Where a feeder supplies continuous loads or any combination of continuous and noncontinuous loads, the rating of the
overcurrent device shall not be less than the noncontinuous load plus 125 percent of the continuous load.
210.20(A) Continuous and Noncontinuous Loads.
Where a branch circuit supplies continuous loads or any combination of continuous and noncontinuous loads, the rating of the overcurrent device shall not be less than the noncontinuous load plus 125 percent of
the continuous load. Exception: Where the assembly, including the overcurrent devices protecting the branch circuit(s), is listed for operation at 100 percent of its rating, the ampere rating of the overcurrent device
shall be permitted to be not less than the sum of the continuous load plus the noncontinuous load.
Something would have to be seriously wrong with your calculations if the service and the main breaker were continuously loaded more than 80%
We were doing a Job once and the home owner wanted to add some things we checked the main breaker and at the time it was loaded to 83% , it was an old home