The standard connector and lock nut should be all you need for the raceway bonding, assuming the raceways are directly attached to a metal enclosure.This is my thought as well. Since there's an SBJ in the generator the load side of the generator terminals get wired just like the secondary of a transformer with no SBJ in the generator switchboard. Each raceway would contain an SSBJ based on the size of the conductors in each parallel raceway.
Last part of the equation, if each raceway where it enters the generator switchboard requires a bonding jumper from the EMT to the EGC bus that can be sized two ways,
One: each raceway would have a bonding jumper sized according to the conductors in each raceway or,
Two: a single bond jumper can be used for all the raceways based on 12.5% of the total kcmils of the parallel conductors.
If you need to install some type of bonding, either way will work, but getting a lug on the bonding bushing for the 12.5% sized conductor might be an issue.