Feeders for meter banks from a switch gearWell, those have to either be feeders or large equipment..
?
Im Not understanding what u mean but thanks for your feedbackLooks good. You should stagger the ins and outs because all of the current is flowing through the small amount of metal between the 4th and 5th conductors.
Even though that's better those connectors are 90° rated I doubt the wire is running at 90 probably 75 so I'd guess that this time won't eventually fail from over usage.
The issue is the choke point within the connector. If you look at the second photo in the OP all of the current is passing through the small amount of metal between the 4th and 5th conductors. Given the conductor size that could possibly be up to 800 amps. At least one manufacturer has a note with their product stating that for larger numbers of conductors they must be arranged similar to the photo in post #6 for that reason. I'll see if I can find the documentation.Even though that's better those connectors are 90° rated I doubt the wire is running at 90 probably 75 so I'd guess that this time won't eventually fail from over usage.
This 100%Looks good. You should stagger the ins and outs because all of the current is flowing through the small amount of metal between the 4th and 5th conductors.
Its 350 al so pretty hard to bend but will keep your tip in mind thanksI would have tried to leave more conductor on the top ones, seems a little "bunched up" to me. One thing you can try is to put the connectors oriented vertical instead of horizontal and do a 90 degree turn into the connectors. Sometimes that gives you flexibility and makes things easier.
Feeding from a switch gear in the basement , to a meter bank on the 15th floor, feeding 15th, 16th and 17th floor apartmentsAre these service conductors or is there a service disconnect ahead of them?
Looks like EMT.No grounds?
Why? Are you required to exceed the NEC?Our AHJ here would want that box bonded at the very least.
What do you mean? It's connected to the EMT which is a great EGC. What else would you Bond it to?Our AHJ here would want that box bonded at the very least.