Existing facility has three phase 240/120V Delta secondary. Two pole mount 15kVAs and one 25kVA transformer.
Customer has increased the size of the building and added significant equipment load in the new area.
The POCO was asked to add a 480Y service to power the new loads.
The POCO said no, can’t have those two services in the same building. Then another POCO employee said yes, if a firebreak wall is added between the two services. This is an open bay work area.
I may have suggested that the POCO view is not supported by the NEC.
Can someone lead me to a rule that supports either view, to help us work with the POCO / AHJ in this unincorporated area.