Im working on a county project for a school. Basically, the project scope is take about (4) building sections (ie. White classroom trailers) and put them together which will then collectively serve as a single classroom for K-12 kids, located on the school site.
Each trailer comes with an individual 100A single phase panel, and there are (4) trailers per group. On my drawings, I showed a feeder coming from the transformer to a disconnect near the transformer, and then im feeding (1) 400A MCB panel located on the assembled sections, and then each panel gets fed from that panel. Overall, very simple.
However, I received a plan review comment that says:
" Service Disconnect(s) nor permitted to be mounted on trailer. NEC 2017, 550.32(A) "
NEC 550.32(A)
(A) Mobile Home Service Equipment. The mobile home ser-vice equipment shall be located adjacent to the mobile home and not mounted in or on the mobile home. The service equipment shall be located in sight from and not more than 9.0 m (30 ft) from the exterior wall of the mobile home it serves. The service equipment shall be permitted to be located elsewhere on the premises, if a disconnecting means suitable for use as service equipment is located within sight from and not more than 9.0 m
(30 ft) from the exterior wall of the mobile home it serves and is rated not less than that required for service equipment in accor-dance with 550.32(C). Grounding at the disconnecting means shall be in accordance with 250.32.
My assumption is that he is referring to section 550.4 (A):
550.4 (A)
General Requirements. (A) Mobile Home Not Intended as a Dwelling Unit. A mobile home not intended as a dwelling unit — for example,
those equipped for sleeping purposes only, contractor’s on-site offices, construction job dormitories, mobile studio dressing rooms, banks, clinics, mobile stores, or intended for the display or demonstration of merchandise or machinery — shall not be required to meet the provisions of this article pertaining to the number or capacity of circuits required. It shall, however, meet all other applicable requirements of this article if provided with an electrical installation intended to be energized from a 120-volt or 120/240-volt ac power supply system. Where different voltage is required by either design or available power supply system, adjustment shall be made in accordance with other articles and sections for the voltage used.
The issue is that if you read the section in its entirety, theres so much within this section that clearly does not apply to a classroom, or any other non-dwelling unit type building. Infact, its pretty clear that it applies strictly to a dwelling unit. In order to cite 550.32(A) as an applicable section, you would have to ignore the other 80% of the same section.
Questions:
THANKS!
NEC 550.32(A)
550.4 (A)
Questions:
- Do you consider a classroom trailer building a "Mobile Home"?
- Would I also have to comply with non-applicable sections within 550 such as 550.10 which states only (1) 50A feeder can be used? Even though the trailers are state permitted and pre-built with multiple 100A panels and demand calcs greater than 50A per panel?
- Why does this section allow for different voltages for design calculations, but later wihtin the same section explicitly states only a 120/240-1 service shall be provided?
- Why is this section so convoluted?
THANKS!