Jpflex
Electrician big leagues
- Victorville
- Electrician commercial and residential
I’m not sure what I’m doing wrong
I have a motor with specs 5 HP, 460 volts, 3 phase, 3.7 watts, 6.33 FLA, power factor 0.82, DES B, ambient temp rise 40 deg cel, service factor 1.15, efficiency 88.5 percent
I use the formula in ugly book to find locked rotor current
KVA not given on label so I figured 3700 watts / KVA (unknown variable x) = 82 percent power factor
so solving for x or unknown gives a KVA of 4,512.19
Formula to find locked rotor current:
1000 x hp x KVA / HP
Top results over or Divided by
Volts (460) x power factor (0.82 percent) x efficiency 88.5 percent x 3 phase (1.732)
= locked rotor current of 8,158.89 amperes
However NEC code book says 46 amperes under TABLE 430.245?