- San Francisco Bay Area, CA, USA
- Electrical Engineer
The overload relay protects based on a time-current curve that is deliberately scaled to be lower than the thermal damage curve of the motor, meaning that the trip will take place BEFORE the motor is damaged and the higher the current the faster it trips. At locked rotor current it would trip in the number of seconds pursuant to the Overload Class; Class 10 trips in 10 seconds, Class 20 trips in 20 seconds, etc. NEMA motors are generally designed as Class 20, IEC motors are all Class 10. So if you have a NEMA design motor, the thermal damage curve can withstand more than 20 seconds at Locked Rotor.
So if you are not using an overload relay, do so. If you are, make sure it is properly sized /adjusted per the manufacturer’s instruction. The concerns from your engineer should be taken care of by understanding this.