I have a 480 volt, 10 kva Delta-Wye transformer to create a neutral for an AC unit. Primary OCPD is 15 amps. Does this require secondary protection?
It's rather convoluted but see Section 240.4(F):I have a 480 volt, 10 kva Delta-Wye transformer to create a neutral for an AC unit. Primary OCPD is 15 amps. Does this require secondary protection?
(F) Transformer Secondary Conductors.
Single-phase (other than 2-wire) and multiphase (other than delta-delta, 3-wire) transformer secondary conductors shall not be considered to be protected by the primary overcurrent protective device...
OK, but say you had a delta-delta transformer. Then 240.4(F) allows you to consider the secondary conductors to be protected by the primary side OCPD (at the proper ratio). Now suppose the B-phase to the primary is lost. As I understand it, that effectively gives you a single phase 2-wire to split phase 3-wire transformer (where the B secondary terminal is now the midpoint of the AB-BC combined coil), for which 240.4(F) would not consider the secondary conductors to be protected by the primary side.But say that the fuse on the B phase to the primary has blown, so that it no longer contributes current to the two windings of the delta primary that it's connected to.
The B terminal is not electrically equal to the midpoint of A-C.OK, but say you had a delta-delta transformer. Then 240.4(F) allows you to consider the secondary conductors to be protected by the primary side OCPD (at the proper ratio). Now suppose the B-phase to the primary is lost. As I understand it, that effectively gives you a single phase 2-wire to split phase 3-wire transformer (where the B secondary terminal is now the midpoint of the AB-BC combined coil), for which 240.4(F) would not consider the secondary conductors to be protected by the primary side.
Therefore it seems that the reason that delta-wye transformers are not permitted to have their secondary conductors protected by the primary OCPD under 240.4(F) would not be related to loss of a primary leg, as that logic would also apply to delta-delta. Or have I overlooked something?
Cheers, Wayne
For a two wire single phase supply connected A-C to a delta-delta transformer? Can you expand on that or point me to a reference that explains the correct answer?The B terminal is not electrically equal to the midpoint of A-C.
I think I see what you mean now, thank you.The B terminal is not electrically equal to the midpoint of A-C.

... Therefore it seems that the reason that delta-wye transformers are not permitted to have their secondary conductors protected by the primary OCPD under 240.4(F) would not be related to loss of a primary leg, as that logic would also apply to delta-delta. Or have I overlooked something?
By significantly, do you mean a factor of sqrt(3), or worse? I have been pursing the math in this thread: https://forums.mikeholt.com/threads...elationships-split-single-phase-case.2574979/The concept I was intending to convey is that in a delta-wye, the ratio of a secondary phase current to the line current feeding the delta can be significantly higher with unbalanced loads than with balanced loads.