FaradayFF
- California
Hello all,
I have a project where there is an existing feeder from an AC panel to a site some distance away. Incoming power to this facility is 208V, 3 phase, 3 wire with equipment ground wire. Currently, they are deriving 120VAC locally by using one phase of incoming power and local ground connection, which I understand is not up to code because you can not use ground as neutral wire. We will need to provide 120VAC to supply 120VAC loads at this facility, since we are doing major rehab and refurbishment work, and so we considered replacing the feeder as part of the scope. Instead of replacing the existing feeder with 208V, 3 phase, 4 wire, can we install a 208V to 208/120V isolation transformer instead. The secondary winding of this isolation transformer would be rated 208/120V and we would be able to supply 3-phase and 1-phase loads as a separately derived system. Going with an isolation transformer, we would not have to replace the feeder to bring it up to code.
Do you see any issues with this approach? It sounds like a cost savor, considering we would need 30kVA or so transformer. Would an isolation transformer be recommended for this project? Would this be treated as a separately derived system?
Thoughts?
Thanks,
EE
Thoughts?
Thanks,
EE