difowler44
Can 14/2 romex be used on residential house with 15amp breakers according to the 2023 NEC? An inspector told me 20amp was the minimum breaker size now for residential. I am in Texas. Code reference please.
(B) 15- and 20-Ampere Branch Circuits.
A 15- or 20-ampere branch circuit shall be permitted to supply lighting outlets, lighting units, or other utilization equipment, or any combination of them, and shall comply with 210.23(B)(1) and (B)(2).
Exception:
The small-appliance branch circuits, laundry branch circuits, and bathroom branch circuits required in a dwelling unit(s) by 210.11(C)(1), (C)(2), and (C)(3) shall supply only the receptacle outlets specified in that section.
(A) 10-Ampere Branch Circuits.
A 10-ampere branch circuit shall comply with the requirements of 210.23(A)(1) and (A)(2).
(1) Loads Permitted for 10-Ampere Branch Circuits.
A 10-ampere branch circuit shall be permitted to supply one or more of the following:
- (1)
Lighting outlets- (2)
Dwelling unit exhaust fans on bathroom or laundry room lighting circuits- (3)
A gas fireplace unit supplied by an individual branch circuit
I'm guessing its not a local code. It was a 3rd party inspector. They wouldn't be able to add to the code book.It would be a local code, I know of a county south of Atlanta that is that way. There are certain circuits that require #12, but the rest can be 15 amp and #14.
Ask him for the code section nicely, saying you would like to learn it. He/she will probably him haw around saying they don’t have it off the top of their head…….The locality can still have amendments they have to enforce, if that’s it, they should be able to give you the amendment section they are enforcing.I'm guessing its not a local code. It was a 3rd party inspector. They wouldn't be able to add to the code book.
When you have a minute please add your location to your profile. Thanks.I am in Texas.
I had that issue on a house many years ago. The owner was a Lowes project manager, and supplied all of the material. Had one box that had 5 three ways in a four gang box for exterior lighting and fans. They didn’t make a romex box deep enough, so I had to use super deep metal cut-in boxes ganged together. A lot of #12’s in that box! LOL!I prefer 14-2 or 3 for lighting, less worries with box fill.
Unlikely do to physical strength and protection issues.When they come out with those 10 amp circuits for the 14 CCA, will they allow 16 copper?
They use that 1.5 mm stuff in the UK on 240v circuits. Have the mechanical properties of it been a problem there?Unlikely do to physical strength and protection issues.
The people over there tend to treat equipment much better than we do hereThey use that 1.5 mm stuff in the UK on 240v circuits. Have the mechanical properties of it been a problem there?
The people over there tend to treat equipment much better than we do here![]()
The properties that need to be discussed are the tensile strength and thermal expansion of the conductors. Of particular concern is the ability of the conductor to withstand the forces resulting from short circuits and the effects of expansion from heat on joints and terminations. Reviewing the information in the table above, you can see that the aluminum conductor will have a cross sectional area 56% larger than copper for the same current carrying capability. Even though aluminum does have a lower tensile strength than copper it can be seen that the AL has, essentially, the same tensile strength of Cu for the same ampacity (50,000 lb/in2). The main area where this would be of concern as stated previously would be strength to withstand the forces during short circuits. Underwriters Laboratory (UL),
So submit a Pubic Input to permit 16 AWG copper for general use. It has been permitted for specific applications for 2 or 3 code cycles.I only checked tensile, copper is supposed to be roughly 40% stronger in tensile, but then I came across this that addresses the two conductors tensile.
I didn't look into the shear strength yet. I don't really see the need for moment or torsion. Copper is also much more ductile than aluminum, and from experience copper seems less likely to work harden and fracture when subject to vibrations.
I love copper lol. Bought an Orange Crate Schwinn with money I got for the copper scrap I picked off my Grandfather's junk pile![]()