That's my experience. I've never driven 2 for detached, but I've got 2 to finish with 2 different (new to me) inspectors. ThanksNothing written, but most inspectors here will let you by with just one rod for a remote building/shed.
Is that a regional thing? Around here it's two rods or 25 ohms or less.Nothing written, but most inspectors here will let you by with just one rod for a remote building/shed.
Same here. It doesn't hurt to ask first.Nothing written, but most inspectors here will let you by with just one rod for a remote building/shed.
Not sure what this means. Are they allowed to make up their own code requirements? Do they not require what is in the NEC?Could be our rocky soil. Difficult to drive rods around here. Plus my inspectors have decades of experience.
I second that.Not sure what this means. Are they allowed to make up their own code requirements? Do they not require what is in the NEC?
But what if lightning struck the underground feeder for the subpanel?I'm only talking about a subpanel in a detached building. If it has it's own service it's 2 rods.
I think the inspectors know the rods do nothing.
They should have to proove it's not 25 ohms or more. Why's it on us to proove it on us to proove that it's less.?Technically yes, unless you have an otherwise adequate grounding electrode system, such as a ufer, (or unless you can prove the first rod is 25 ohms or less to earth, which is not worth bothering with).
250.32 requires a grounding electrode system for the building, according to the same rules (250 Part III) as for a building with a service.
The requirement for a 2nd supplemental electrode is 250.53(A)(3).
Well that would make a good fireball!But what if lightning struck the underground feeder for the subpanel?
250.53A says IF multiple rods…….Technically yes, unless you have an otherwise adequate grounding electrode system, such as a ufer, (or unless you can prove the first rod is 25 ohms or less to earth, which is not worth bothering with).
250.32 requires a grounding electrode system for the building, according to the same rules (250 Part III) as for a building with a service.
The requirement for a 2nd supplemental electrode is 250.53(A)(3).
I have to tell you, even with my field of ground rods and my lightning arrestors, my ham radio tower always made me nervous during thunder storms. One time during a snow storm I saw a lightning arrestor spark across it's air gapWell that would make a good fireball!
Which 14 more rods wouldn't stop!!!
Supplemental requirement is 250.53(A)(2). Typo above.250.53A says IF multiple rods…….