Is it permissible per NEC to splice together an Equipment Ground Conductor (EGC) and a Grounding Electrode Conductor (GEC) to make use of a common wire to serve both purposes?
We have an upstream Panel A which is going to feed a new panel B location that was previously just a tap block used to distribute branch circuits. Because of existing grounding circuits and conduits already installed the contractor wants to spice the new ECG for the new Panel B (fed from panel A) to an existing GEC used for the required GEC on a downstream panel fed from a SDS transformer. Because this downstream panel (Panel C) was previously installed it already had this GEC in place connected to a common ground bar in close proximity.
The attached sketch hopefully shows what I am referring to more clearly. From the sketch is it permissible to splice the required EGC to panel B to the existing GEC to provide a EGC patch all the way back up to Panel A (through existing ground bar) as shown on sketch?