arc_flashed
- FL, United States
I have seen this brought up in a few other threads so I apologize for any overlap, but I am still confused and hoping someone can help me out with understanding.
I have a 75kva 208/120vac wye transformer inside a facility. The question comes up with quantity of current carrying conductors and the wire sizing from the secondary of this transformer to the distribution panel. Does the neutral count as a current carrying conductor between the transformer secondary and the 200amp main breaker on my panel? Standard 75degC would make this a 3/0 conductor unless you apply the 80% for 4 CCCs.
I understand a 3-phase load with a neutral would not count under 310.15(E)(1) (2024 edition of NFPA) but my panel is made up of 100% single phase loads (all receptacles).
Since all my loads are 1P (H, N, G = 2CCCs) and connected to the panel's neutral bus, wouldn't my transformer X0, and therefore my neutral conductor, carry all of this current and need to be counted as a current carrying conductor pushing me to an 80% conductor rating?