Christoph
Master Electrician, Code Official
- Coopersburg, PA
- Electrical Inspector
Hello,
I am looking for some insight on how to best solve this issue:
I was called to a pool pump breaker that keeps tripping when it is hot out. These are the parameters (from the top so to speak):
In looking it over and doing some math I come up with a required breaker size of 100A and separate thermal protection for the motor. There is no thermal protection I can see anywhere. I doubt the motor has integral thermal protection (I am not great with motor controls).
My questions:
Thank you.
Christoph
- 2-pole 40A Type CH GFI breaker in a load center
- 6AWG THHN in 1/2” conduit
- Non-fusible disconnect
- 7 1/2 hp motor (nameplate attached, sorry for the poor resolution (single phase 230V, 1.15 SF continuous duty))
- Reading 29A operating current when I got there. Was running for hours before I got there
- Outside temp was about 85°F
My questions:
- How would you solve the thermal overload issue? Are there better or worse solutions for motor starters?
- How would you provide GFI protection for the motor if I were to put a 100A breaker in (which my boss is already fighting me on. He said he has never put anything bigger than 125% FLC/FLA breaker in for a motor.)
- Is excessive heat a factor in higher operating currents for motors and that’s what would trip the breaker?
Thank you.
Christoph