rc/retired
- Bellvue, Colorado
- Master Electrician/Inspector retired
YepYes, attached at the bottom edge of the joist
Just treat it like a sheetrock ceiling
Yep.I would install the smoke alarm at the bottom of the stairs. A CO detector is not required unless there's a bedroom. Per building code.
Barring any local amendments, of course.
Ron
You need a CO detector if you have fossil fuel fired appliances. That water heater qualifies.I would install the smoke alarm at the bottom of the stairs. A CO detector is not required unless there's a bedroom. Per building code.
Ron
Correct. The building code requires the CO detector to be installed near the entrance to bedrooms.You need a CO detector if you have fossil fuel fired appliances. That water heater qualifies.
I have the wires run for interconnection already. I probably forgot to make that clear. My main question was about clearance from the water heater. Here we have from reply #3:Do not forget interconnection.
That seems to apply to all stoves, whether gas or electric, but I guess there is no similar requirement for water heaters?Smoke alarms and smoke detectors shall not be installed between 10 ft (3.0 m) and 20 ft (6.1 m) along a horizontal flow path from a stationary or fixed cooking appliance
So finished basement2. On every occupiable level of a dwelling unit, including basements.
It says occupiableEvery basement. There is no mention of a distinction between an unfinished and a finished basement In R314 or R315 or Chapter Two Definitions.
That doesn't fit with the wording "occupiable level"CRC definition
[RB] OCCUPIED SPACE. The total area of all buildings or structures on any lot or parcel of ground projected on a horizontal plane, excluding permitted projections as allowed by this code.
Yes, but that phrase "occupiable level" indicates that there are some levels which are not occupiable. Such as unfinished basement.I guess it takes faith in doing the right thing. Would you concede that an occupiable level is also an occupiable space?
A crawl space could be considered not occupiable. An unfinished basement with a washing machine and dryer is certainly occupiable. Likewise with a water heater and HVAC equipment. And how unfinished does it have to be? My basement is 1/3 finished, 1/3 unfinished, and 1/3 an attached garage. You could certainly put a chair, or even a bed in the 1/3 unfinished space.Yes, but that phrase "occupiable level" indicates that there are some levels which are not occupiable. Such as unfinished basement.
And I'm curious about the use of both words, occupiable and occupied. Is there a contextual reason?