- New Jersey
- Journeyman Electrician (retired)
We have a 480, 200 HP fire pump controller fed with a single 3 conductor, #4/0 Vitalink about 300' in length. From T430.250 the motor draws 240 amps so the #4/0 is too small. We're being told that we need to upgrade the feeder to 3-#350 single conductor Vitalink. (I didn't check the calculation factoring in the VD requirement). They want to abandon the existing 3C, #4/0 cable and run three new single #350 kcmil Vitalink cables. I suggested just running a second 3C, #4/0 parallel to the existing but that was met with a luke warm response. Anyone have an opinion on which method is better? Looks like the contractor will be on the hook for the cost so to me the single additional cable is a no brainer.