Hypothetical situation you have a dozen PV panels on a roof, panels are marked with a open circuit voltage of 23.5.
The panels are wired in parallel, system is ungrounded and runs at about 14.4 volts.
At some point after some fused disconnects the voltage is stepped up to 48 Volts with a DC/ DC converter.
I have the following questions about this scenario:
If a PV system is never over 30 Volts does it inherently meet the rapid shutdown 30 volt requirement ?
In a system with no inverter, but does have a DC to DC converter where do the 'PV system circuits' end and a DC feeder begin?
A first disconnect?
The panels are wired in parallel, system is ungrounded and runs at about 14.4 volts.
At some point after some fused disconnects the voltage is stepped up to 48 Volts with a DC/ DC converter.
I have the following questions about this scenario:
If a PV system is never over 30 Volts does it inherently meet the rapid shutdown 30 volt requirement ?
In a system with no inverter, but does have a DC to DC converter where do the 'PV system circuits' end and a DC feeder begin?
A first disconnect?