I seem to recall a code section essentially limiting the sum of the main circuit breakers for an MLO panel acting as a main. I dont run into this often. Anyone know what code section this is, assuming im not incorrectly remembering.
The situation is an existing condition for an Electrical service being re-built and it needs to be designed to work using the existing infrastructure if possible.
I have a 480/277v, 1200A, main MLO panel with:
(1) 500A/2P
(1) 400A/2P
(1) 800A/3P
(1) 300A/2P
So in total, this comes up to 2000A, however most of the breakers are single phase. Depending on the code (if there is one). If this were adjusted to account for the service being 3-phase then this would be about 1500A @ 480/3.
Either way, any issue with 2000A / 1500A sum of mains on a 1200A MLO panel?
Any help appreciated.
(1) 500A/2P
(1) 400A/2P
(1) 800A/3P
(1) 300A/2P